Fire Engineering Training Community

Where firefighters come to talk training

What do you all us for your engineers field operations? We use the rule of eights and have some cheats that we memorize to go with those cheats.

Views: 4298

Reply to This

Replies to This Discussion

Hi Colin,

We developed a simple "rule of thumb" friction loss for our engineers. 1-1/2 hose is 30 psi per 100
1-3/4 hose is 20 psi per 100
2-1/2 hose is 10 psi per 100
3 hose is 5 psi per 100
All you have to add is your nozzle pressure and lenght of line and you are all set!
We use 50 psi nozzles for our 1-3/4. we carry 200 ft with nozzle, FL=40+ Np 50 = 90/100 Pump discharge pressure.
Some engineers have marked the gauges for normal pump ops, knowing if at the add a line they know how much to adjust the pump throttle.

Come visit me a "Let's Talk Pumps", FDIC, Thursday 1030-1215, Room 206-207
Hope this helps,
Bob Franklin
+1 on what this guy said.

If you really want to know what you're flowing you're going to have to get the flow meter and pitot gauge. Every fire apparatus has different bends, valves, and whatnot even if they're sister vehicles. The point here is even if you have the same exact trucks they'll flow different. The pitot and flow meter are you're best bet to get the correct pressures.

If you don't want to go that route due to financials or whatever get in touch with the hose, nozzle, and appliance vendors and get their data. It won't be the most accurate but it's better than the hand method or generic formulas. My opinion. Good luck bro.

Adam Miceli said:
I'd second running your own tests and developing your own cards. We've found that different hose and discharges have a significant difference in FL. We use the C Formulas as a baseline, but nothing beats a calibrated flow meter and pitot gauge to determine actual friction loss and preset gauges.
Bob Franklin said:
Hi Colin,
We developed a simple "rule of thumb" friction loss for our engineers. 1-1/2 hose is 30 psi per 100 1-3/4 hose is 20 psi per 100
2-1/2 hose is 10 psi per 100
3 hose is 5 psi per 100
All you have to add is your nozzle pressure and lenght of line and you are all set!
We use 50 psi nozzles for our 1-3/4. we carry 200 ft with nozzle, FL=40+ Np 50 = 90/100 Pump discharge pressure.
Some engineers have marked the gauges for normal pump ops, knowing if at the add a line they know how much to adjust the pump throttle.

Come visit me a "Let's Talk Pumps", FDIC, Thursday 1030-1215, Room 206-207
Hope this helps,
Bob Franklin
Bob, did you guys test your hose and pumps to validate your numbers? In particular the 1.75" FL you show as 20 psi by formula would be accurate at less than 125 gpm and the 3" FL at 5 psi is theoretically/mathematically correct for under 335 gpm both far less GPM than normally flowed through the respective hoses. Again, these number could very well be true given newer hose tends to be "oversize" in dia. and liners tend to create much less drag than older types. We've found a huge difference in our three types of 1.75" hose all between 35-72 psi FL @ 185 gpm per 100 ft.
Pump operators at the University Fire Department are trained to memorize a given set of GPM's, Frictions losses and operations and use a standard equation for hydraulic calculations. We train so that operators have a thorough understanding of field hydraulics and when they become certified on the apparatus they can choose to use cheat sheets. Most members will carry a dry erase marker, that helps with doing the equations.

Reply to Discussion

RSS

Policy Page

PLEASE NOTE

The login above DOES NOT provide access to Fire Engineering magazine archives. Please go here for our archives.

CONTRIBUTORS NOTE

Our contributors' posts are not vetted by the Fire Engineering technical board, and reflect the views and opinions of the individual authors. Anyone is welcome to participate.

For vetted content, please go to www.fireengineering.com/issues.

We are excited to have you participate in our discussions and interactive forums. Before you begin posting, please take a moment to read our community policy page.  

Be Alert for Spam
We actively monitor the community for spam, however some does slip through. Please use common sense and caution when clicking links. If you suspect you've been hit by spam, e-mail peter.prochilo@clarionevents.com.

FE Podcasts


Check out the most recent episode and schedule of
UPCOMING PODCASTS

© 2024   Created by fireeng.   Powered by

Badges  |  Report an Issue  |  Terms of Service