We are looking at changing SOG for FDC connections. At what starting pressure does your engineers start with when addressing a connection?

Views: 212

Replies to This Discussion

It depends on whether you are supplying the sprinklers or a standpipe. For sprinklers, we use 150 PSI regardless. This is the state standard from the state fire marshal. For standpipes, our hose pack (150 ft X 1&3/4 inch with wye and solid bore nozzle) gets charged at 120 PSI + 25 for the standpipe + 5 PSI per fllor of elevation. In most cases we use 150 PSI then add 10 is needed.
My department usually deploys a hotel pack the consists of 150' of 1 3/4 with a standard fog nozzle. The hydraulics work out to 175 psi pump pressure and that does not include head pressure. All the engineer has to do is add 5 lbs. per floor to reach the proper pump pressure.

RSS

Policy Page

PLEASE NOTE

The login above DOES NOT provide access to Fire Engineering magazine archives. Please go here for our archives.

CONTRIBUTORS NOTE

Our contributors' posts are not vetted by the Fire Engineering technical board, and reflect the views and opinions of the individual authors. Anyone is welcome to participate.

For vetted content, please go to www.fireengineering.com/issues.

We are excited to have you participate in our discussions and interactive forums. Before you begin posting, please take a moment to read our community policy page.  

Be Alert for Spam
We actively monitor the community for spam, however some does slip through. Please use common sense and caution when clicking links. If you suspect you've been hit by spam, e-mail peter.prochilo@clarionevents.com.

FE Podcasts


Check out the most recent episode and schedule of
UPCOMING PODCASTS

Groups

© 2024   Created by fireeng.   Powered by

Badges  |  Report an Issue  |  Terms of Service