Kirk Allen

62, Male

Kansas, Illinois

United States

Profile Information:

Lives in:
Kansas, Illinois
Department:
Kansas Fire Protection Distirct
Title/rank:
Chief
Years of public service:
25
Agency structure:
Volunteer fire department
Top issues in your department:
Mandatory training
Professional Qualifications:
Retired AF, Chief Fire Officer, Hazmat, EMT
Topics you provide training for:
Suppression, Hydraulics, RIT, Grain bin Rescue
Areas of expertise:
none :)

Comment Wall:

Load Previous Comments
  • Larry Lasich

    Yes Sir, That was me.

    I have been trying to get anyone to listen when I say that we don't KNOW for sure what we are getting from the pumpers.

    I have asked for flow meters and in line pressure gauges, but I get the "Budget" response. I'm now trying to get containers to clock the flow against, but today I was out running the rig by myself. There is not a lot of interest in getting real numbers right now.

    PS I did find the name brand of the 1.75 inch hose that we run on our attack lines (Key 800) and got the reported friction loss from the PDF file on your website. Thanks for that info.
    Now I'm getting "It can't be that high, the nozzles are flowing what they are supposed to, yada".

    Thanks for your response,
    Larry
  • Kirk Allen

    Do you have a truck scale near by? Any place with a truck scale might let you put the pumper on the scale, weigh it full then flow water for a given time, then do the math on the weight after flowing. Its crude but it will tell you flow. The problem with that is it wont tell you where the problems are.

    I feel your pain on no one listening. The FL numbers we see in some brands of hose is criminal. Not even close to the forumlas.

    Another option is if you have hydrants in your area you can use city funds to get a flow meter to "TEST" the hydrants. Then once they buy into that you will have a flow meter to use for anything else you want to test.

    And the old seet of the pants as to how long it takes to drain the tank with the handline gets you close and I have had some argue that it was one number until they were blue in the face only to confused when I asked how much water was still in the hose, plumping and pump before they shut down the pump? They just dont seem to understand all the variables in between the tank and their nozzles.

    Dont get discouraged because even after showing people with flow meters and pressure guages I have been accused of "rigging" the flowmeter to show poor numbers for their stuff.

    Its a week position at best but some people just arent open to the truth.

    When Bobby Halton was the Training Chief in Albuqerque they were flowing 75 gpm, not 150+ as they thought. What seperates the leaders from the followers in this business is what they do with that kind of information. Chief Halton ended up flow testing EVERYTHING and made changes to ensure they were getting the flows they expected. The followers just ignore the facts. Those are the ones that scare the hell out of me.

    Let me know how I can help.

    Thanks
    Kirk
  • Kirk Allen

    Any chance your coming to FDIC?

    Shoot me a good address and I will get you a couple inline pressure gauges to use.

    I place one in the preconnect and the other at the inlet of the nozzle. Bring your static pressure up to 100psi and make sure all the gauges on the panel and those installed are reading within 5psi. We commonly see panel gauges way off because they never get tested so we never know when they're off.

    Then when flowing water, assuming your pumping 150 on the #1 discharge. If the gauge in the preconnect reads 120, then your losing 30psi of loss before the pressure even gets to the hose.

    Next read the pressure at the nozzle. If it reads 100 psi, then you now know the "measured" loss in the hose, which for this crude example, is 20psi of loss, yet most folks would take the discharge pressure of 150 and subrtract the nozzle pressure and insist the hose FL is 50 instead of using the actual hose inlet pressure of 120. They just fail to take into account the plumbing.

    Remeber that as the flow goes up, so too with the FL, expenentialy.