Recently a discussion in the Start Water Group go me to thinking. I know several of our discussions have been about nozzle choice, mainly smoothbore or fog nozzle, but what about the differences in smoothbores? For those of you who already have smoothbore nozzles, which one do you use and why?

Views: 150

Replies to This Discussion

the high rise packs in NHRFR use the breakaway solid bore nozzle that can be adapted for use as a fog. The fog tip is kept in the hi rise bag (it might not even be in there anymore). The nozzle is a 1" tip reduced down to 15/16" with a St' Louis adapter screwed on. It works well in the residentials where we don't get hit with the blast furnace of the winds on the cliffs either overlooking the Hudson river or the meadowlands. The first three engines bring in the hi rise packs (2" line) and then all additional engines bring in 100' of 2-1/2" line with smooth bore nozzle. We figure if we can't knock it down by that time, it is time to bring out the heavy artillery. Most FD's don't like to admit it, but most "real" hi rise fires go out when they burn down to a point where we can approach them (thermal elimination of the fuel). Still, if the small lines are not making it, whether fog or SB, soemone has to have the sense ot leash the hounds, close the doors, and let the fire cinder-ize the apt. If it is that hot, no one is alive anyway -- nothing to be gained -- not worth the risk
We are using the Akron ball valve shutoff with 1 1/8" tip. In field testing we found that the smooth ball valve made a better stream than the split ball valve another manufacture offers. It may not be enough to be an operational difference but creates enough turbulence to make quite a visible difference in stream quality. I also did not like the slide valve offered by TFT. This makes for a nice looking stream but a very small water way. This small water way would not pass debris and is a clog point. It is very important during standpipe operations to reduce areas debris could block or reduce the flow of water.
Back to tip size. the 1 1/8 has about 99 pounds of reaction force and seems to be manageable. Some fire department use the 1 1/4 tip. This tip size is moving into master stream territory by some definitions at 325gpm and has about 126 pounds of RF and is far less forgiving when over pressurized. I do however like the "Indy" tip. it's a 1 1/8" screwed onto a 1 1/4". The 1 1/8" can be used for that interior attack and the 1 1/4" reserved for more defensive or outside operations.

RSS

Policy Page

PLEASE NOTE

The login above DOES NOT provide access to Fire Engineering magazine archives. Please go here for our archives.

CONTRIBUTORS NOTE

Our contributors' posts are not vetted by the Fire Engineering technical board, and reflect the views and opinions of the individual authors. Anyone is welcome to participate.

For vetted content, please go to www.fireengineering.com/issues.

We are excited to have you participate in our discussions and interactive forums. Before you begin posting, please take a moment to read our community policy page.  

Be Alert for Spam
We actively monitor the community for spam, however some does slip through. Please use common sense and caution when clicking links. If you suspect you've been hit by spam, e-mail peter.prochilo@clarionevents.com.

FE Podcasts


Check out the most recent episode and schedule of
UPCOMING PODCASTS

Groups

© 2024   Created by fireeng.   Powered by

Badges  |  Report an Issue  |  Terms of Service