Fire pumps (that are rated in the USA) are rated in Gallons per Minute of draft at sea level. Therefore a 1250 GPM pump will lift 1250 GPM of water, somewhere between 22 to 33 feet at sea level. If you are drawing water from a pressurized hydrant, you are getting what ever the hydrant can send you. If you are getting your water from a water carrier, it will be somewhere in the middle.
To answer your question, we need to know what your water supply situation is.
Larry
Girish Raj:
There are three variables that must be met when testing fire pumps. First, is the lift. As you have indicated you are drafting at a 3 meter (about 10 ft.) which is the correct set-up for a fire pump in the U.S. Second, you must reach the 10 Bar (150 psi) discharge pressure. Lastly, you must discharge the correct volume from the nozzle or nozzles. Since we are discussing a 4,000 lpm pump it is possible to use a single 50mm (2”) diameter nozzle. A 2” (50 mm) nozzle at 79 psi (5.37 bar) nozzle pressure will flow 1057 gpm. You must use a pitot tube to measure the nozzle discharge through the 50 mm tip.
The discharge volume and the pump pressure are inter-related because the nozzle pressure is not the same as the pump pressure, and by simple math, we find that we must loose 71 psi between the pump and the nozzle opening. This is accomplished by the “friction loss” found in appliances, hose, pump piping and by throttling back the discharge valves on the pump.
Most U.S. pumps are designed to flow 250 gpm (1,000 lpm) per discharge, although the piping may be capable of 500 gpm or more, so let us assume you are feeding this 2” nozzle with two (2) – 6.3 cm lines (2 ½”) hoses, each 15 meters (50 ft.) long.
Procedure: Get your pump primed and begin flowing water through the 2” nozzle. Be certain to have this securely tied to a stationary object, as the reaction force when fully supplied will be about 500 lbs. Have an assistant monitor the pitot at the nozzle and throttle up until you achieve the correct flow when the pitot reads 5.37 bar. Check your engine pressure which should now be between 115 psi (7.8 bar) and 140 psi (9.5 bar). Alternately bump the discharge valves slightly toward the closed position. The pitot pressure will drop slightly, so raise the engine pressure slightly to bring the nozzle pitot back to the desired 79 psi. Continue this until the engine pressure is at 150 psi and the nozzle pitot is at 79 psi. Record the engine rpm and hold the system stable for the specified time to prove that the cooling system and motor are capable of meeting the specification.
If, as you indicate, you wish to use all 5 discharges, attach a 1” (25 cm) nozzle to each outlet and use the pitot to set each nozzle at 50 psi (3.4 bar) hold the engine at 10 bar and close the discharges until the nozzles all read 50 psi on the pitot gauge. (211 gpm per nozzle)
Bill
The login above DOES NOT provide access to Fire Engineering magazine archives. Please go here for our archives.
Our contributors' posts are not vetted by the Fire Engineering technical board, and reflect the views and opinions of the individual authors. Anyone is welcome to participate.
For vetted content, please go to www.fireengineering.com/issues.
We are excited to have you participate in our discussions and interactive forums. Before you begin posting, please take a moment to read our community policy page.
Be Alert for Spam
We actively monitor the community for spam, however some does slip through. Please use common sense and caution when clicking links. If you suspect you've been hit by spam, e-mail peter.prochilo@clarionevents.com.
Check out the most recent episode and schedule of UPCOMING PODCASTS
45 members
116 members
62 members
73 members
166 members
65 members
277 members
510 members
10 members
106 members
© 2024 Created by fireeng. Powered by
FE Home | Product Center | Training | Zones | Fire-EMS | Firefighting | Apparatus | Health/Safety | Leadership | Prevention | Rescue |