1-3/4" vs. 2-1/2" Hi-rise pack - Fire Engineering Training Community2024-03-19T13:20:17Zhttps://community.fireengineering.com/forum/topic/show?commentId=1219672%3AComment%3A75192&id=1219672%3ATopic%3A75134&feed=yes&xn_auth=noJeff, buy David McGrails book…tag:community.fireengineering.com,2011-07-20:1219672:Comment:4355132011-07-20T19:14:49.564ZRuss Chapmanhttps://community.fireengineering.com/profile/RussChapman
Jeff, buy David McGrails book Standpipe Operations from Penwell. You will never need to read another book about the subject. All your answers too anyone's arguments will be addressed there.
Jeff, buy David McGrails book Standpipe Operations from Penwell. You will never need to read another book about the subject. All your answers too anyone's arguments will be addressed there. I just came across your post…tag:community.fireengineering.com,2011-07-20:1219672:Comment:4350922011-07-20T05:39:30.664ZJeff Lewishttps://community.fireengineering.com/profile/JeffLewis
<p>I just came across your post about 2 1/2 after a small dispute about friction loss. would love to see your PP. Thanks Jeff</p>
<p>frostywite@aol.com<br></br> <br></br> <cite>Robert Owens said:</cite></p>
<blockquote cite="http://community.fireengineering.com/forum/topic/show?commentId=1219672%3AComment%3A75887&id=1219672%3ATopic%3A75134#1219672Comment76059"><div>We also have both. Typically we use the 2 1/2 for large commercial occupancies that are uncompartmented, and anything with stand pipe…</div>
</blockquote>
<p>I just came across your post about 2 1/2 after a small dispute about friction loss. would love to see your PP. Thanks Jeff</p>
<p>frostywite@aol.com<br/> <br/>
<cite>Robert Owens said:</cite></p>
<blockquote cite="http://community.fireengineering.com/forum/topic/show?commentId=1219672%3AComment%3A75887&id=1219672%3ATopic%3A75134#1219672Comment76059"><div>We also have both. Typically we use the 2 1/2 for large commercial occupancies that are uncompartmented, and anything with stand pipe operations.<br/> <br/>
We use the 1 3/4 for leader lines (which we deploy mostly on multi family dwellings), and small compartmented commercial occpancies like food service etc.<br/>
<br/>
I love the 2 1/2 and think it is one of the most underutlized and trained on tools in the fire service.<br/>
<br/>
Shoot me your email and I will email you the Power Point presentation we used to introduce it to our FD and all of the testing we did with it.</div>
</blockquote> Hey Mike,
I agree with the 2…tag:community.fireengineering.com,2008-09-12:1219672:Comment:792612008-09-12T18:34:26.582ZMike Walkerhttps://community.fireengineering.com/profile/MikeWalker
Hey Mike,<br />
<br />
I agree with the 2 1/2" guys. GPM puts the fire out. So many times the information the first arriving companies recieve upon arrival is going to be sketchy at best, so they probably won't know exactly what they are dealing with from the ground floor. Also, any information they recieve is old information as far as the fire is concerned and will be even older by the time crews reach the fire. The fire could be MUCH larger then reported by the time crews get to it. Another point that…
Hey Mike,<br />
<br />
I agree with the 2 1/2" guys. GPM puts the fire out. So many times the information the first arriving companies recieve upon arrival is going to be sketchy at best, so they probably won't know exactly what they are dealing with from the ground floor. Also, any information they recieve is old information as far as the fire is concerned and will be even older by the time crews reach the fire. The fire could be MUCH larger then reported by the time crews get to it. Another point that must be considered is that your people can only carry up so much equipment. If you load them down like pack mules with all the different "options" they may make it to the correct floor but they likely will be too tired to work. It's far better to streamline what they take up. We use a 200 ft. 2 1/2" with 1 1/4" smoothbore, and the appropriate appliances. Small fires can be put out with the larger line as you know but a small line can't put out a large fire. Dave McGrail's book on High-Rise and Standpipe buildings is a fantastic text, I highly recommend it. This text will help you communicate many of the aspects of High-Rise to those members of your department who will resist changing. When we were upgrading to the correct equipment I came up quite a bit of opposition to the smoothbore nozzle. The M&M test McGrail explains in his book will help them see the light. If that doesn't work, take them to one of your older buildings, have them flow the line. After 45 minutes of seeing brackish water flow, not to mention the smell, they will soon realize that the fog nozzles are going to clog and clogged nozzles will kill firefighters. Also, you might check out the High-Rise Group. Maybe some of the discussions there will help you. Oh! One last point. I've been finding out that the pressure needed for the smaller lines tend to cause failures in combination sprinkler/standpipe systems. Those systems are only as strong as their weakest soldered joint, and boy do they make a mess. Bro
I did not read all the po…tag:community.fireengineering.com,2008-09-12:1219672:Comment:791732008-09-12T12:09:58.283ZRuss Chapmanhttps://community.fireengineering.com/profile/RussChapman
Bro<br />
I did not read all the posts, but I also want to put my 2 cents in for 2 1/2" hose. Manpower should not be an issue when it comes to standpipe operations, as the fire will be in a class 1 or 2 building by the most part, and contained. Either by default, or by design you should wait for a second engine company. Due to EWD (extreme wind drivin fires) phenomenon, the ladder companies should NOT open up until told to do so by the engine company officers. So there is some manpower right…
Bro<br />
I did not read all the posts, but I also want to put my 2 cents in for 2 1/2" hose. Manpower should not be an issue when it comes to standpipe operations, as the fire will be in a class 1 or 2 building by the most part, and contained. Either by default, or by design you should wait for a second engine company. Due to EWD (extreme wind drivin fires) phenomenon, the ladder companies should NOT open up until told to do so by the engine company officers. So there is some manpower right there.<br />
One point I want to make to everyone is that all l standpipe kits should contain an inline gauge. This is not a "nice" thing to have, but should be a mandatory safety tool. It takes the onus off the pump operators, and identifies water problems, which in my opinion, outside of health and MVA LODD issues, is the leading killer of FFs. You DEFINATLY need inline gauges when you use 2 1/2" hose.<br />
Be safe if your looking for info on s…tag:community.fireengineering.com,2008-09-12:1219672:Comment:791632008-09-12T04:23:09.749Zdoug ricehttps://community.fireengineering.com/profile/doc
if your looking for info on standpipe operations Andy Fredricks and Dave Mcgrail have many great articles on this topic archived on this web site and on Firenuggets.com. Doug
if your looking for info on standpipe operations Andy Fredricks and Dave Mcgrail have many great articles on this topic archived on this web site and on Firenuggets.com. Doug Many departments choose 1 3/4…tag:community.fireengineering.com,2008-09-11:1219672:Comment:789772008-09-11T01:55:10.577ZRayhttps://community.fireengineering.com/xn/detail/u_1nlpq12q7dtpg
Many departments choose 1 3/4 hose for standpipe operations for the wrong reasons. Can an 1 3/4 line extinguish a fire in a fire resistant building? Of course. But thats is not the problem. The problem as stated by others is the pressure needed to get 200' of 1 3/4 up and running. 2 1/2" hose is much more forgiving and will see you through the tough ones also. When you attach your wye to the riser so you can supply two 1 3/4 lines. Think about the pressure thats required. I would rather have…
Many departments choose 1 3/4 hose for standpipe operations for the wrong reasons. Can an 1 3/4 line extinguish a fire in a fire resistant building? Of course. But thats is not the problem. The problem as stated by others is the pressure needed to get 200' of 1 3/4 up and running. 2 1/2" hose is much more forgiving and will see you through the tough ones also. When you attach your wye to the riser so you can supply two 1 3/4 lines. Think about the pressure thats required. I would rather have one 2 1/2. mike,
i would consider using…tag:community.fireengineering.com,2008-09-09:1219672:Comment:787432008-09-09T19:17:49.369Zjohn wakie jr.https://community.fireengineering.com/profile/john23
mike,<br />
i would consider using a 2 1/2 inch line for all high rise building fire proof buildings. These fires have a tendancy to blow torch out of a room into the hallway, if wind driven. In studies that were recently condcted by the FDNY the recreated a wind driven fire using a large fan out side a window the tempture in the common hallway went from 73 degrees to 1200 floor to celing in 45 seconds! A 2 1/2 inch line will also deliver a larger volume of water which will reduce knowdown time…
mike,<br />
i would consider using a 2 1/2 inch line for all high rise building fire proof buildings. These fires have a tendancy to blow torch out of a room into the hallway, if wind driven. In studies that were recently condcted by the FDNY the recreated a wind driven fire using a large fan out side a window the tempture in the common hallway went from 73 degrees to 1200 floor to celing in 45 seconds! A 2 1/2 inch line will also deliver a larger volume of water which will reduce knowdown time significantly. hope this helps you out -john Ladder 104 F.D.N.Y. thanks for the extra info. my…tag:community.fireengineering.com,2008-08-25:1219672:Comment:761942008-08-25T21:13:48.078ZMichael Scanzerahttps://community.fireengineering.com/profile/MichaelScanzera
thanks for the extra info. my email is mscanzera@aol.com if i can get a copy of that powerpoint presentation that would be awesome. thanks again for the info!!!<br />
<br />
-mike
thanks for the extra info. my email is mscanzera@aol.com if i can get a copy of that powerpoint presentation that would be awesome. thanks again for the info!!!<br />
<br />
-mike We also have both. Typically…tag:community.fireengineering.com,2008-08-25:1219672:Comment:760592008-08-25T13:29:55.247ZRobert Owenshttps://community.fireengineering.com/profile/RobertOwens
We also have both. Typically we use the 2 1/2 for large commercial occupancies that are uncompartmented, and anything with stand pipe operations.<br />
<br />
We use the 1 3/4 for leader lines (which we deploy mostly on multi family dwellings), and small compartmented commercial occpancies like food service etc.<br />
<br />
I love the 2 1/2 and think it is one of the most underutlized and trained on tools in the fire service.<br />
<br />
Shoot me your email and I will email you the Power Point presentation we used to introduce…
We also have both. Typically we use the 2 1/2 for large commercial occupancies that are uncompartmented, and anything with stand pipe operations.<br />
<br />
We use the 1 3/4 for leader lines (which we deploy mostly on multi family dwellings), and small compartmented commercial occpancies like food service etc.<br />
<br />
I love the 2 1/2 and think it is one of the most underutlized and trained on tools in the fire service.<br />
<br />
Shoot me your email and I will email you the Power Point presentation we used to introduce it to our FD and all of the testing we did with it. Glad this helped. We are fort…tag:community.fireengineering.com,2008-08-25:1219672:Comment:759692008-08-25T01:52:26.662ZRicky Teterhttps://community.fireengineering.com/profile/RickyTeter
Glad this helped. We are fortunate enough to run 4 person engine crews, an engineer, an officer and two muckers on the back step. With the Officer and the two muckers we can deploy our 200' of 2 1/2". I'm not going to lie and say it is easy you bust your rear, but with training it can be done. We are also lucky enough to have 4 person truck companies also and most truck crews are pretty good about grabbing some line and helping advance as they are moving forward to their assignments.<br />
<br />
Our shop…
Glad this helped. We are fortunate enough to run 4 person engine crews, an engineer, an officer and two muckers on the back step. With the Officer and the two muckers we can deploy our 200' of 2 1/2". I'm not going to lie and say it is easy you bust your rear, but with training it can be done. We are also lucky enough to have 4 person truck companies also and most truck crews are pretty good about grabbing some line and helping advance as they are moving forward to their assignments.<br />
<br />
Our shop has done a great job creating brackets inside the cab of our apparatus that we hang our packs on, our packs are set up in 50' hoseshoe loads so they hang nicely on the racks as well as on our cylinders while we are carrying them and the brackets keep them out of the way.